Dimension |
2U
Height: 86.5 mm (3.4 inches)
-
Depth: 763.7 mm (30.1 inches)
Note: The depth is measured
with rack latches installed, but without the security bezel installed.
|
Weight |
Up to 28.0 kg (61.7b), depending on the server
configuration |
Processor (depending on the model) |
For a list of supported processors, see: Lenovo ServerProven website
Note:
All processors on the system board must be of the same type,
and have the same speed, number of cores, and frequency.
For server models with twelve 3.5-inch drive bays, Intel® Xeon® 6240C processor is not supported.
For server models with 550-watt ac power and two processors,
the TDP limitations of each processor vary with the drive bay configurations:
Eight 2.5-inch drive bays: no more than 125 watts
Eight 3.5-inch drive bays: no more than 125 watts
Twelve 2.5-inch drive bays: no more than 105 watts
Sixteen 2.5-inch drive bays: no more than 85 watts
When you install a processor, follow below rules to select
a heat sink:
|
Memory |
For 1st Generation Intel ® Xeon ® Scalable Processors (Intel ® Xeon ® SP
Gen 1):
For 2nd Generation Intel ® Xeon ® Scalable
Processors (Intel ® Xeon ® SP Gen 2):
For a list of supported DIMMs, see: Lenovo ServerProven website
Note:
Operating speed and total memory capacity depends on the processor
model and UEFI settings.
When four DCPMMs are installed, ensure that the processor TDP
is lower than or equal to 125 watts.
|
Operating systems |
Supported and certified operating systems:
For a complete list of operating systems, see:
OS Interoperability Guide
For OS deployment instructions,
see: Deploy the operating system.
|
Internal drives |
The supported drives vary by models.
Up to eight 3.5-inch simple-swap SATA drives
Up to eight 3.5-inch hot-swap SAS/SATA drives
Up to twelve 3.5-inch hot-swap SAS/SATA/NVMe drives (NVMe drives
supported only in drive bays 8–11 if a 3.5-inch AnyBay backplane is
installed)
Up to sixteen 2.5-inch hot-swap SAS/SATA/NVMe drives (NVMe
drives supported only in drive bays 4–7 if a 2.5-inch AnyBay backplane
is installed)
Up to two 3.5-inch hot-swap SAS/SATA drives in the rear (supported
only by server models with 12 drive bays in the front)
Up to two M.2 drives
Note:
Server models installed with either one processor or two processors
support Non-Volatile Memory Express (NVMe) SSDs. For the server model
installed with one processor, one AnyBay backplane, and one PCIe switch,
no more than four NVMe SSDs can be installed.
Rear hot-swap SAS/SATA drives are supported only when the processor
TDP is lower than or equal to 105 watts.
|
Expansion slots |
One PCIe slot on the system board
Two riser card slots on the system board
Two or three PCIe slots on the riser card
For detailed information, see Rear view.
|
Input/Output (I/O) features |
Front panel:
Rear panel:
One VGA connector
One XClarity Controller network connector
One serial port (available on some models)
Two USB 3.0 connectors
Two Ethernet connectors
Two Ethernet connectors on the LOM adapter (available on some
models)
|
RAID/HBA adapters (depending on the model) |
SAS/SATA HBA adapters
ThinkSystem 430-8i SAS/SATA 12Gb HBA
ThinkSystem 430-16i SAS/SATA 12Gb HBA
ThinkSystem 430-8e SAS/SATA 12Gb HBA
ThinkSystem 430-16e SAS/SATA 12Gb HBA
ThinkSystem 440-8i SAS/SATA PCIe Gen4 12Gb HBA
ThinkSystem 440-16i SAS/SATA PCIe Gen4 12Gb HBA
ThinkSystem 440-16e SAS/SATA PCIe Gen4 12Gb HBA
ThinkSystem 4350-8i SAS/SATA 12Gb HBA
SAS/SATA RAID adapters
ThinkSystem RAID 530-8i PCIe 12Gb Adapter
ThinkSystem RAID 530-16i PCIe 12Gb Adapter
ThinkSystem RAID 540-8i PCIe 12Gb Adapter
ThinkSystem RAID 540-16i PCIe Gen4 12Gb Adapter
ThinkSystem RAID 730-8i 1GB Adapter
ThinkSystem RAID 730-8i 2GB PCIe Adapter
ThinkSystem RAID 930-8i 2GB Flash PCIe 12Gb Adapter
ThinkSystem RAID 930-16i 4GB Flash PCIe 12Gb Adapter
ThinkSystem RAID 930-16i 8GB Flash PCIe 12Gb Adapter
ThinkSystem RAID 930-8e 4GB Flash PCIe 12Gb Adapter
ThinkSystem RAID 940-8i 4GB Flash PCIe Gen4 12Gb Adapter
ThinkSystem RAID 940-8e 4GB Flash PCIe 12Gb Adapter
ThinkSystem RAID 940-16i 4GB Flash PCIe Gen4 12Gb Adapter
ThinkSystem RAID 940-16i 8GB Flash PCIe Gen4 12Gb Adapter
ThinkSystem RAID 5350-8i PCIe 12Gb Adapter
ThinkSystem RAID 9350-8i 2GB Flash PCIe 12Gb Adapter
ThinkSystem RAID 9350-16i 4GB Flash PCIe 12Gb Adapter
Note:
A software RAID controller is integrated on the system board.
The software RAID controller supports JBOD mode and RAID levels 0,
1, 5, and 10.
RAID 730-8i 1G Cache SAS/SATA adapter is not available for
North America.
RAID 530-8i SAS/SATA adapter cannot be mixed with RAID 730-8i
1G Cache SAS/SATA adapter.
RAID 730-8i 2G Flash SAS/SATA adapter cannot be mixed with
RAID 730-8i 1G Cache SAS/SATA adapter or RAID 930-8i SAS/SATA adapter.
The RAID 940 adapters can be mixed with the ThinkSystem 440-8i
SAS/SATA PCIe Gen4 12Gb HBA and the ThinkSystem 440-16i SAS/SATA PCIe
Gen4 12Gb HBA.
Mixing of RAID/HBA 430/530/730/930 adapters (Gen 3) and RAID/HBA
440/540/940 adapters (Gen 4) in the same system is not allowed.
RAID 930/940 series or 9350 series adapters require a RAID
flash power module.
RAID 4350/5350/9350 series adapters cannot be mixed with HBA/RAID
430/440/530/540/730/930/940 series SAS/SATA adapters.
|
System fans |
Note:
For server models with twelve 3.5-inch drive bays and has one
of following processors installed, if one fan fails, replace it with
a new fan to avoid cooling problems: Intel Xeon 5122, 6140, 6140M,
6152, 8156, 8158, 8160, 8160M, 8164, 6242, 6240, 6248, 6252, or 6210U.
If your server comes with only one processor, three system
fans (fan 1 to fan 3) are adequate to provide proper cooling. However,
you must keep the location for fan 4 occupied by a fan filler to ensure
proper airflow.
|
Power supplies (depending on the model) |
One or two hot-swap power supplies for redundancy
support
550-watt ac 80 PLUS Platinum
750-watt ac 80 PLUS Platinum
750-watt ac 80 PLUS Titanium
|
Electrical input |
Note: For server models with 750-watt ac 80 PLUS Titanium power
supplies, 100–127 V ac input voltage is not supported.
CAUTION:
240 V dc input (input range: 180-300 V dc) is supported in
Chinese Mainland ONLY.
Power supply with 240 V dc input cannot support hot plugging
power cord function. Before removing the power supply with dc input,
please turn off server or disconnect dc power sources at the breaker
panel or by turning off the power source. Then, remove the power cord.
In order to for the ThinkSystem products to operate error free
in both a DC or AC electrical environment, a TN-S earthing system
which complies to 60364-1 IEC 2005 standard as to be present or installed.
|
Minimal configuration for debugging |
- One processor in processor socket 1
- One memory DIMM at slot 3
- One power supply
- Three system fans (fan 1 to fan 3)
|
Acoustical noise emissions |
Sound power level, idle
4.6 bels, minimum
4.8 bels, typical
5.9 bels, maximum
Sound power level, operating
4.7 bels, minimum
4.8 bels, typical
5.9 bels, maximum
Note:
These sound power levels are measured in controlled acoustical
environments according to procedures specified by ISO 7779 and are
reported in accordance with ISO 9296.
The declared acoustic noise levels are based on specified configurations
and they may change depending on configurations/conditions.
The declared acoustic noise levels may increase greatly, if
high-power components are installed, for example, some high-power
NICs, CPUs, and GPUs.
|
Environment |
The server is supported in the following environment: Note: This server is designed for standard data center environment and
recommended to be placed in industrial data center.
Air temperature:
Maximum altitude: 3050 m (10 000 ft)
Relative humidity (non-condensing):
Particulate contamination
Attention: Airborne
particulates and reactive gases acting alone or in combination with
other environmental factors such as humidity or temperature might
pose a risk to the server. For information
about the limits for particulates and gases, see Particulate contamination.
Note:
Your server complies with ASHRAE class A2 specifications. The
server performance might be impacted if one system fan fails. For
server models with twelve 3.5-inch drive bays, if one system fan fails,
the following Intel Xeon processors are not supported: 5122, 6140,
6140M, 6152, 8156, 8158, 8160, 8160M, 8164, 6242, 6240, 6248, 6252,
or 6210U.
Depending on the hardware configuration, some models comply
with ASHRAE class A3 and class A4 specifications. To comply with ASHRAE
class A3 and class A4 specifications, the server model must meet the
following requirements at the same time:
Two power supplies are installed.
No system fan fails.
Rear hot-swap drive is not installed.
NVMe drive is not installed.
DCPMM memory is not installed.
For server models with twelve 3.5-inch drives, M.2 drive is
not installed when the operating temperature is outside ASHRAE class
A3 specifications.
The following processors are not installed: Intel Xeon 6136,
6140, 6140M, 6142, 6142M, 6148, 6152, 8158, 8160, 8160M, 8160T, 8164,
6242, 6240, 6248, 6252, or 6210U. For a list of supported
processors, see: Lenovo ServerProven website
|